We are trying to get a single M-Style Smartmotor commanded over a rs-485 network. The motor is a SM23165MT-IP version 5.98.3.61 We can command it using the SMI software with no problem. We are hooked up to an AB compactlogix L32E through a Ethernet IP to Ascii realtime automation gateway. When we send the command "RPA" out from the compactlogix The smartmotor receives the command and acts like it ignores it. We can type the command in the terminal window and the smartmotor responds correctly. Not sure what we are missing any help would be appreciated.

Daryl

Re: RS-485 Communication problem M-Style motor 2 years, 7 months ago #1422

  • csearcy
  • OFFLINE
  • Posts: 480
  • Karma: 23
Hi Daryl,
If you open up the Serial Data Analyzer in SMI2 you can see exactly what is being sent to the motor with the RPA command. If the motor address is 1, it actually sends Hex81 before the RPA. Hex80 is global, Hex81 is Motor1, Hex82 is Motor2, etc.

Re: RS-485 Communication problem M-Style motor 2 years, 7 months ago #1423

Wish I could figure out a way to send a snap shot of the Serial data analyzer. This is what I see in the window. Address of the motor is 1

>81 52 50 41 0D |..RPA..

Daryl

Re: RS-485 Communication problem M-Style motor 2 years, 7 months ago #1424

  • csearcy
  • OFFLINE
  • Posts: 480
  • Karma: 23
That's what I expected you would see. So you have to send Hex81 before the RPA and follow it with a carriage return which is Hex0D.

Re: RS-485 Communication problem M-Style motor 2 years, 7 months ago #1425

A little confused..... The first characters are Hex81 and the last Set is Hex0D. The command does include those values. Are you saying to follow the Hex81 with a carriage return as well?

Re: RS-485 Communication problem M-Style motor 2 years, 7 months ago #1426

  • csearcy
  • OFFLINE
  • Posts: 480
  • Karma: 23
No... the string coming out of your ASCII converter should look just like what you see in the serial data analyzer.