TOPIC: Motor will "RUN?"...but it will not "RUN"

Motor will "RUN?"...but it will not "RUN" 5 months ago #2256

SM2316MT-IP-DN firmware 5.97
The motor will not RUN it's program the "Z" command is issued
It WILL run when the "RUN?" is the first line and the RUN command is issued from the serial line

Have exhausted all sample code... Cannot get the motor to run at startup.

Re: Motor will "RUN?"...but it will not "RUN" 5 months ago #2258

  • csearcy
  • Posts: 480
  • Karma: 23
You need to have Drive Enable tied to 24VDC on the I/O port. If you can't run it with the SMI Playground (considering you have to either used limit switches or disable them with the EIGN(2) EIGN(3) commands) you need to check for faults or a Drive Off condition.